Skip to main content
Cart

KB-TZ II 3/4 Dia Profis

Posted by Anthony Kongalmost 3 years ago
KB-TZ II 3/4 Dia Profis

KB-TZ II doesn't show larger diameter anchors in Profis. How can I use anchors larger than 5/8?

Hilit Profis,KB-TZ II,3/4 diameter

1 Reply
Posted by Danielle Fileralmost 3 years ago
Hilti Verified

Hi Anthony,

It's possible that is the largest anchor diameter we have tested for the application you are looking at. For clarification and assistance, please send your .pe file to Hilti's engineering team at hnatechnicalservices@hilti.com. Additionally, you may reference ICC ESR-4266 for concrete or ICC ESR-4561 for masonry applications to see if the diameter is listed for your application.

Regards,
Dani

KB-TZ2,KB-TZ2 PROFIS Engineering