Intumescent paint thickness for a HSS column

Posted by Audrey McNamaraalmost 3 years ago
Intumescent paint thickness for a HSS column

What is the required thickness to achieve a 2-HR rating on an HSS 3x3x3/16 ? Which products can be used to achieve this?

Intumescent coatings,Firestop thickness

1 Reply
Posted by Rudy Jarvisover 2 years ago
Hilti Verified

Good afternoon Audrey,

Unfortunately there is currently not sufficient testing to support a 2-hr rating on a 3" x 3" x 3/16" HSS with the Hilti Intumescent Steel Protection Coatings as it is smaller that what has been tested. Your best option would likely be to use a Cementitious Fireprotection Spray or a gypsum column enclosure. Let me know if you need anything further.

Thank you,


Rudy Jarvis


Fire Protection Engineering TeamHilti North America

3701 W. Royal Lane, Suite 100 I Irving, TX, 75063P 1-800-879-8000 I F 918-254-1679

E usfirestopeng@hilti.com

www.us.hilti.com/firestop

steel protection,HSS column