Intumescent Paint Product for 3hr Columns

Posted by Blair Onyekanneabout 7 years ago
Intumescent Paint Product for 3hr Columns

Hi, I am looking at your intumescent paint data. My W Flange columns need to be rated 3hrs, but I only see up to 2hr assemblies for columns. (Design No. Y633) 

Am I supposed to use Design No. 640 to reach 3hr rating on my columns?

Hilti Fire Finish,intumescent paint,3 hour protection

4 Replies
Posted by Ernst Toussaintabout 7 years ago
Hilti Verified

Hello Blair and thank you for posting your question on ASK Hilti. With regards to 3 hour listing for Wide Flange Columns, we have 3 hour ratings in our UL listing under our Y633. I have attached a copy of our new UL listing for your records which should answer your question. If you need additional information, please contact the Steel Protection Engineering Team at Usspeng@hilti.com.

Ernst.


2 comments on this reply
Posted by Ernst Toussaintalmost 6 years ago
Good morning Will and thank you for posting your question regarding beams on ASK Hilti. Yes, we do have a Beam listing that includes a 3 hour beam test. Please send me an email at Usspeng@hilti.com so I could provide you the Beam Listing. Best regards, Ernst.

Posted by Will Thompsonalmost 6 years ago
Hello Ernst, In review of Y633 it shows testing for columns. Is there testing for steel W section beams also? We would require a 3 HR rating for application being considered. Thank you, Will Thompson

Posted by Ernst Toussaintover 5 years ago
Hilti Verified

Also, the N640 UL Design can only be used for beams that are supporting a fire-resistance-rated, concrete-over-metal-decking floor assembly (the floor assembly will affect the exposed perimeter of the Steel Member, and raise the massivity (W/D) of the steel member. This is why there is less fireproofing required for the same size of member compared to the Y33 UL Design). You can obtain those 3 hour beam ratings per unrestrained or restrained data that is listed in the file. If you have additional questions, please send our engineering team your questions at Usspeng@hilti.com.

Best regards,

Ernst.


Posted by Jim McAuliffeover 5 years ago

Hello- Is there a design for 3 hour beams? I need a basis of design product for possible exposed beams in my project.


Posted by Josh Muckenhirnover 4 years ago

Hello, does this also apply to HSS columns instead of wide flange? I am looking for 3HR rating for a HSS column.


1 comment on this reply
Posted by Ernst Toussaintover 4 years ago
Good afternoon Josh and thank you for reaching out to hour Hilti Platform. We do have a UL listing for 3 hour HSS columns and it is utilizing our Y634 UL Design for the application of the Fire Finish 120 product. Could you please send an email to our engineering team at Usspeng@hilti.com so they can provide you a copy of this listing? Unfortunately we are unable to attach documents to this chain. Best regards, Ernst.