Intumescent Coating at Column meeting beam with SFRM above

Posted by Carol Kuongabout 4 years ago
Intumescent Coating at Column meeting beam with SFRM above

Are there a UL listing or test performed that we can apply intumescent coating on a steel column, that is directly supporting an existing steel beam fireproofed with spray applied fire resistive material? They are not the same structural member, so I would like to know if a test has been performed or an EJ is required.

steel column,Intumescent coatings

1 Reply
Posted by Perla Salcedoabout 4 years ago

Hello Carol, the UL listing you can use for the column is UL Y633. Since you have two fireproofing martials, one on the beam and potentially Hilti intumescent on the column you can apply Hilti intumescent to the column and overlap it on to the beam and current fireproofing. For more details and testing supporting this method, please reach out to us via the Hilti Steel Protection email: usspeng@Hilti.com

Thank you,

Perla V. Salcedo, MS
Testing and Sales Support Engineer
Hilti North America 

steel protection,Intumescent coatings