Posted by Leonard Schlosser11 months ago
Intall Torque Requirement for KB-TZ2 installed in Lightweight Concrete

Does the lightweight reduction apply to the install stall torque requirements of KB-TZ2 anchors?

ANCHORS,lightweight,KB-TZ2

1 Reply
Posted by Sinan Beskok11 months ago
Hilti Verified

Hi Leonard,

Thank you for reaching out. The installation torque values for the Kwik Bolt TZ2 (KB-TZ2) listed in the Instructions for Use as T_inst,concrete would apply to both lightweight and normal-weight concrete conforming to Section 3.2 of ESR-4266.