Insulated Pipe Penetration U336 Wall

Posted by Tyree Vantreaseover 1 year ago
Insulated Pipe Penetration U336 Wall

I need a 2 hour rated penetration assembly for insulated 3" steel pipes in a U336 wall. I've found W-L-1406c but that does not include insulated pipes. Is there a variation that does?

Penetration,insulation,U336

1 Reply
Posted by JESSICA STARKSabout 1 year ago
Hilti Verified

Tyree,

Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs. The only system we have for this wall type is W-L-5259, which does not match your exact application.
 
As such, we can address your application through an Engineering Judgment which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
 
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.) 
 
Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti Firestop Selector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or ask a Question anytime, anywhere. You can download the app on the Google Play Store and Apple App Store. 
 
If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.

Thank you,

Jessica Starks
Senior Fire Protection Engineer