In Hilti Profis value of Tau_k does not match value from ESR report

Posted by Sterlingover 3 years ago
In Hilti Profis value of Tau_k does not match value from ESR report

Reviewing the calculations from a report in Hilti Profis. I have threaded stainless stud 0.75 diameter with hammer drill in low temperature setting. In the bond calculation the values of Tau_k, (cracked and uncracked) do not seem to match what I see in the ESR. In the PROFIS calcs these are:
t k,c,uncr =2,533 psi
t k,c = 1,387 psi (page 4)
However, in the ESR, i see the following:
t k,c,uncr =2,130 psi
t k,c = 1,250 psi (page 18)

ESR-3814,PROFIS values dont match ESR

2 Replies
Posted by Emily over 3 years ago
Hilti Verified

Hi Sterling,

For further assistance, please email your inquiry and .pe file to hnatechnicalservices@hilti.com.

Regards,
Emily


Posted by STEVE HAYMOREover 2 years ago

Was any explanation ever given for why Profis uses values of tau that don't match those provided in the ESR report? I have the same concern / question.