How does ACI 318-19, Section 17.1.6 come into play, if rebar is developed, how do we account for breakout?

Posted by SHADY REZKALLAabout 3 years ago
How does ACI 318-19, Section 17.1.6 come into play, if rebar is developed, how do we account for breakout?

How does ACI 318-19, Section 17.1.6 come into play, if rebar is developed, how do we account for breakout?
What is the point of developing the rebar then?

concrete breakout failure,Anchorage/development length

1 Reply
Posted by Danielle Filerabout 3 years ago
Hilti Verified

Hi Shady,

Please see this article, which discusses the design of reinforcing bars under anchoring to concrete provisions. ACI 318-19 17.1.6 applies to reinforcing bars that are being used as anchorage. If you are developing the yield strength of reinforcing bars for the purpose of concrete reinforcement, then Chapter 25 would be applicable. Breakout behavior of straight reinforcing bars as a group is analogous to tension and shear breakout behavior of adhesive anchors. Anchor reinforcement provided in accordance with 17.5.2.1 may be used to prevent concrete breakout failure.

Regards,
Dani

17.1.6,Reinforcing bars anchoring provisions