Hot to use Profis to Design a single anchor without torsion?

Posted by Bill H.about 4 years ago
Hot to use Profis to Design a single anchor without torsion?

I have a three legged tank. Each leg has one anchor hole. When I try to evaluate one anchor, it get the error that a single anchor construction cannot be used with torsion. This occurs whenever I apply a shear load to the anchor. I have no torsion in the anchor.
How can I check this anchor point that has both tension and shear in it using Profis?
Thanks for your help, Bill Holloway PE, wfh_pe@hotmail.com

Single anchor,no torsion

2 Replies
Posted by Ashley Couronabout 4 years ago
Hilti Verified

Hi Bill,
 
For further assistance, please email your “.pe” file to hnatechnicalservices@hilti.com.
 
Regards,
Ashley


Posted by Bill H.about 4 years ago

I believe that I found the issue. It had to do with the profile not being eccentric. The off center profile created the torsion in the evaluation. If the  profile is centered on the baseplate, the error message goes away. If the profile is a channel or angle, chances are it would be installed off center of the baseplate.

profile,eccentricity,Torsion