Skip to main content
Cart

Hitting Rebar In Cooling Tower Basin during Epoxy anchor installation

Posted by Patrick Anastasioover 4 years ago
Hitting Rebar In Cooling Tower Basin during Epoxy anchor installation

Post installation of Hilti Epoxy Anchors resulting in hitting reinforcement steel.

anchor,EPOXY,REbar,drill,scanning

1 Reply
Posted by Ashley Couronover 4 years ago
Hilti Verified

Hi Patrick,
 
If you are hitting reinforcing bars during anchor installation, it is recommended to inform the Engineer of Record for the project. The decision on how to proceed with the installation and the location of the anchors is up to the Engineer of Record for the project. For further discussion on anchor installation near abandoned holes, please refer to this answer from a previous question.
 
Regards,