Hilti PROFIS Anchor Calculation of psi (cp,N)

Posted by Terry Braxmeierabout 3 years ago
Hilti PROFIS Anchor Calculation of psi (cp,N)

Please refer to the uploaded output file. Under section 3.2 Concrete Breakout Failure, psi (cp,N) - listed as 0.792. The values listed for hef, ca(min) , and cac are also listed. In using those values in ACI 318-14 Eq. (17.4.2.7b) that is also provided above the values tabulations, we are getting 0.656 for psi (cp,N). What is the program doing that causes this discrepancy?

Hilti Profis not matching hand calculations,ACI 318-14 Eq. 17.4.2.7b

1 Reply
Posted by Danielle Filerabout 3 years ago
Hilti Verified

Hi Terry,

The software is using the hef,act of 120.7 mm from Page 1 of the report for the calculations. When you use this hef for the calculations, you should get the same result at PROFIS Engineering.

Regards,
Dani

profis engineering,hef,actual,act