Skip to main content
Cart

Hilti KIWK HUS EZ Capacities in Grouted CMU -Masonry Strengths

Posted by Brian Murthaover 2 years ago
Hilti KIWK HUS EZ Capacities in Grouted CMU -Masonry Strengths

I have reviewed the tech guide for the Hilti KIWK HUS EZ's capacities in grouted CMU. It appears that the allowable loads are based off of a minimum masonry strength of 1500psi. If a stronger masonry (f'm) is provided, can the allowable loads increase? If so, please provide relevant information.

Masonry,Kwik HUS EZ

1 Reply
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Brian,

The testing that Hilti has for the KH-EZ installed into grout-filled CMU with a compressive strength of 1,500 psi. If you are going to be installing into grout-filled CMU with a higher compressive strength, Hilti does not have any specific testing for other CMU blocks of a different compressive strength. Therefore, you would need to use your engineering judgement and/or on-site testing to verify the capacity of the anchoring system.

If you have further questions, please reach out to hnatechnicalservices@hilti.com.

Regards,
Ashley

Kwik HUS EZ