Why is the KB3 wedge anchor NOT available to use in Profis? The catalog for KB3 says to use Profis to optimize the design when there are multiple load adjustment factors, but KB3 is not an option in Profis.

KB3 Wedge Anchors,Missing KB3

1 Reply
Posted by Danielle Filerabout 3 years ago
Hilti Verified

Hi Tom,

The KB3 anchor is approved for use in uncracked concrete only. PROFIS Engineering might be filtering out the KB3 if you have cracked concrete selected. If you need additional assistance, please email your .pe file to hnatechnicalservices@hilti.com.