Hilti HDI and HD-L allowed for seismic

Posted by  LJover 1 year ago
Hilti HDI and HD-L allowed for seismic

Hilti HDI and HD-L allowed for seismic per IBC seismic cat D?

drop in anchor,Seismic allowed

3 Replies
Posted by Matthew Fordover 1 year ago
Hilti Verified

Hi LJ, 

The HDI and HDI-L drop-in anchors are not seismically approved. However, the HDI-P TZ and HDI-TZ drop-in anchors are approved from seismic conditions. For more information, please reference ESR-4236.

Regards,
Matthew

Flush Anchors

Posted by  LJover 1 year ago

Thank you. I have additional question; can I embed the drop-in anchor deeper to increase the concrete breakout capacity?

drop in anchor,increasing embedment depth

Posted by Matthew Fordover 1 year ago

Hi LJ,

Hilti has not performed testing with drop-in anchors beyond the published embedment depth values, so anchor performance is unknown. It would ultimately be up to the engineer on the project to evaluate the anchors and determine if they are suitable for the given application.

Regards,
Matthew

Drop-In Anchor