Groups of Exp. Anchors in underside of CMD in pure Tension

Posted by Jeff Stevensover 6 years ago
Groups of Exp. Anchors in underside of CMD in pure Tension

Is there an additional reduction factor for groups of exp. anchors anchored to the underside of metal deck? Also, the anchoring to CMD module for PROFIS has a button for 2 anchors, but does not output any results for the second anchor. Will this be added?

anchor group,Pullout,soffit

1 Reply
Posted by PARIS STANTONover 6 years ago
Hilti Verified

Hi Jeff,

As long as you meet the spacing requirements, there are no additional reduction factors for groups of anchors. Currently, analyzing two anchors in the soffit of COMD is outside the scope of the software, however, I will pass your request on to our software team.

Regards,
Paris

COMD