Firestopping requirements per IBC Section 715.1 at Exterior Non-Firerated Wall and Floor Assembly

Posted by GLEN MORGENWECKover 3 years ago
Firestopping requirements per IBC Section 715.1 at Exterior Non-Firerated Wall and Floor Assembly

Condition is a non-firerated exterior metal stud assembly with gypsum sheathing by-passing concrete floor slab. As the metal studs are set slightly out from the face of slab edge to allow the gypsum board to by-pass the slab edge, a small void occurs as illustrated by the attached detail, which is shown in red. On the interior of this wall, the 5/8" gypsum board will extend to the deck and be caulked with non-firerated sealant.

In review of IBC 2018 Section 715.1, fire-stopping and/or perimeter joint system is not required per exception 7 as the exterior wall is non-firerated. Is this a correct interpretation or should the void be filled with "material"?

perimeter joint system,perimeter firestopping

1 Reply
Posted by Shazi Shahabiover 3 years ago
Hilti Verified

Hi Glen,
Thanks for your firestop request. This is a great question, but we need to look further into the details of the condition. Would you please send an email to USfirestopeng@hilti.com, and we can discuss the condition further more.
 
Thanks in advance,
Shazi Shahabi

perimeter firestopping