Firestop Systems for Pipe Penetration Thru Concrete Wall for OSHPD

Posted by Royce Kuromoto5 months ago
Firestop Systems for Pipe Penetration Thru Concrete Wall for OSHPD

What is the recommended firestopping system to use for pneumatic tubing thru an existing concrete wall that is pre-approved by HCAI/OSHPD?

concrete,firestop,OSHPD,OPM

2 Replies
Posted by JESSICA STARKS5 months ago
Hilti Verified

Royce,

As there is no listed system for this condition, our recommendation would be to request for a custom detail in the form of an Engineering Judgment (EJ) that will reflect your exact condition. Systems should be used only when they match your exact application, so this is a situation when an EJ is required. We provide hundreds--if not thousands--of details yearly for HCAI/OSHPD projects and should be able to support you once you submit your request.

Thank you,

Jessica Starks
Lead Fire Protection Engineer


Posted by Sydney Riopel5 months ago
Hilti Verified

Hello,

Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.

We do not have listed systems for pneumatic tubing through a concrete wall; however, we can address your application through an Engineering Judgment, which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.

Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)

If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.

Thank you,

Sydney Riopel
Fire Protection Engineer


1 comment on this reply
Posted by Royce Kuromoto5 months ago
Hi Sydney or whom it may concern, Thank you for that information. What is your recommendation for a firestop system for a penetration thru a concrete wall for pneumatic tubing in lieu that there is no system specific for pneumatic tubing or custom fits. Would it be acceptable to provide C-AJ firestop system to route the pneumatic tubing thru the concrete wall? Thanks, Royce