Firestop in conduits

Posted by Joey Beyerover 6 years ago
Firestop in conduits

I have a few conduits that penetrate a concrete floor or a 2 hour rated partition that is full of cables and would need a system to use for firestopping inside the conduit. The conduit is rigid steel and the cable fill exceeds 45%, I found the other system with mineral wool and FS One Max. Is there a system for when the cables exceed the 45% fill?

conduit,Cables

1 Reply
Posted by Nicholas Rischerover 6 years ago

Joey,

Thank you for reaching out, yes we do have a few systems for when the cables exceed the 45%fill.

Please reference the attached systems "CAJ3320, CAJ3281, CAJ3216, CAJ3210 and CAJ3208", all of these systems will meet your requirements for cable fill greater than 45%.

If you have any other questions please let us know

Nicholas Rischer

Fire Protection Engineering Team
Corporate Engineering

Hilti North America