Firestop HVAC duct through roof / ceiling assembly

Posted by James Whitridgealmost 5 years ago
Firestop HVAC duct through roof / ceiling assembly

Looking for a firestop detail for a HVAC roof duct penetrating horizontal gypsum board attached to the bottom of wood 2x roof joist that provides a 1-hour protection for the wood roof joists.

Ceiling,non-rated rood deck

1 Reply
Posted by Tyler Thomasalmost 5 years ago
Hilti Verified

Hello James,
Please see attached system F-C-8026 for HVAC lineset through a common UL design L500 series wood floor/ceiling assemblies. It sounds like you have UL design P500 series wood roof/ceiling assembly. We don't have any system for P500 but we can create an engineering judgment based on F-C-8026 by changing the horizontal assembly to P500 assembly to match your application. We can also show the engineering judgment as the HVAC is penetrating through a rated gypsum ceiling only, it doesn't have to show the roof. If you would like an engineering judgment, please follow the instruction below to submit a request for an engineering judgment.

Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/content/hilti/W1/US/en/engineering/design-centers/firestop/engineering-judgments.html (US) or https://www.hilti.ca/content/hilti/W1/CA/en/engineering/design-centers/firestop/engineering-judgments.html (Canada.) 
 
For instructions on how to register along with how to navigate the new platform, please see the attached document: EJ FAQ.
 
If you have any questions, please reach out to our customer service team at 1-800-879-8000 for assistance.