Firestop for existing CMU wall pipe penetrations

Posted by HW10 months ago
Firestop for existing CMU wall pipe penetrations

Hello, I am seeking a firestop system that would work for metallic pipe penetration into an existing CMU wall. It is unknown whether the CMU is UL classified. Please advise if/which firestop can be used.

3 hour,Existing CMU,Firestop CMU

2 Replies
Posted by Anthony Nguyen10 months ago
Hilti Verified

Hello Hannah,

Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs. One of the most common systems we reference when there's a metallic pipe penetrating through a concrete wall/CMU wall is WJ1067 for 1 or 2 hour fire-rating, depending on the thickness of the wall assembly. Although your CMU wall assembly is not UL Classified, we may still be able to provide you with a rated solution through an Engineering Judgement.

The HILTI CONSTRUCTION PLATFORM (HCP) is the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: hilti.com/ej (US) or hilti.ca/ej (Canada.)

Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti Firestop Selector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or ask a Question anytime, anywhere. You can download the app using the appropriate link below.

Hilti Firestop Selector App – Google Play Store

Hilti Firestop Selector App – Apple App Store

If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance or use the following link to access the How-To Videos for HCP on YouTube: Hilti Fire Protection Software How-To Videos Playlist


Thank you,
Anthony Nguyen
Fire Protection Engineer

firestop,concrete wall

Posted by HW10 months ago
Hilti Verified

Hi Anthony, I would like to submit my question through Engineering Judgement. What would be the charge for this service? Thank you.


1 comment on this reply
Posted by Chase Hellan10 months ago
Hi there is no charge for EJ services. Thank you Chase