See attachment for stacked walls. What fire-stopping joint would be required between CMU and metal studs/gypsum board?
Greetings Ken,
Thank you for using ASK Hilti!
It looks like your attachment did not come through unfortunately. However, based on the description of the application you provided, I have attached WWS-0048 which addresses how to treat the joint for a gypsum wall stacked on top of a CMU wall. You can review this system and see if they work for your application.
If they do not, we can review your application for an Engineering Judgment (EJ). An Engineering Judgment is a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)
For instructions on how to register along with how to navigate the new platform, please see the attached User Guide.
If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.
Thank You for choosing Hilti as your Firestop Experts!
Best Regards,
Tri Truong
Fire Protection Engineering Team