Fire Stop Detail for Structural I-Beam Penetrating Rated Assembly

Posted by Jason Dillabout 6 years ago
Fire Stop Detail for Structural I-Beam Penetrating Rated Assembly

Do you have a detail for fire stop around a structural I-Beam that is penetrating a rated assembly?

1 hour firestop,I-Beam

1 Reply
Posted by Chase Hellanabout 6 years ago
Hilti Verified

Hello Jason,

I have attached W-L-7188, and W-J-7110 for gypsum wall and concrete wall/block wall assemblies, respectfully. Both of these are non fire rated I beams, if you have firepoofing (either Monokote or intumscent) you will need to submit for an Engineering Request (form is also attached).

Thank you,
Chase

firestop,Structural