Posted by Jason Dillabout 6 years ago
Fire Stop Detail for Structural I-Beam Penetrating Rated Assembly
Do you have a detail for fire stop around a structural I-Beam that is penetrating a rated assembly?
1 Reply
Posted by Chase Hellanabout 6 years ago
Hello Jason,
I have attached W-L-7188, and W-J-7110 for gypsum wall and concrete wall/block wall assemblies, respectfully. Both of these are non fire rated I beams, if you have firepoofing (either Monokote or intumscent) you will need to submit for an Engineering Request (form is also attached).
Thank you,
Chase