Is my customer able to remove the "1" Gyp. Liner to cover installation gap" and the sheet of Drywall above the corridor ceiling?
They would then fire safe inside the stud cavity from the ceiling to the deck. Is this something they can do to keep the rating?

Fire Rating,Engineering

1 Reply
Posted by Sydney Riopel3 months ago
Hilti Verified

Hello,

Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.

Hilti’s firestop scope is to restore the fire rating of an assembly at penetrations and joints. Because the rating of the actual wall or floor assembly is determined by the design professional or project specifications, we typically rely on the information provided to us when an engineering judgment request is submitted. For this reason, Hilti does not have internal tools for identifying the fire rating of this assembly, and we defer to standard third-party resources.

If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.

Best regards,

Sydney Riopel