Posted by RAUDEL MARINalmost 3 years ago
Fire-Rated Joint Compound for Wall-to-Wall Joint

Is there a fire-rated joint compound that can be applied to a wall-to-wall joint? I have a condition where two pieces of gypsum board joint but there is a 1/8" gap between them. In order to maintain the fire and smoke rated system I'm looking for a product that can fill the 1/8" gap between the two pieces of gypsum board. 


joint,wall-to-wall

1 Reply
Posted by Austin Griffithalmost 3 years ago

Greetings Raudel,



Thank you for using ASK Hilti!


We currently off multiple products that sound like
they would work for your situation. However, if you are looking to use a listed
firestop systems, our only current gypsum to gypsum system would be WW-D-0067
utilizing CP 606 and mineral wool. If this system does not work for you, we
would be happy to provide you with an engineering judgement to fully encompass
your situation. While we may be able to provide a solution for you, please note
that our systems and engineering judgements are not to designed to replace when
mud and tape is required. If you would like to submit for an engineering
judgement, this can be done through www.hilti.com/EJ


 If you have any questions firestop related,
please reach out to our customer service team at 1-800-879-8000 (US) or
1-800-363-4458 (Canada) and ask to speak to the firestop team for assistance.
We would be happy to walk you through the details of any firestopping Hilti
UL/cUL listed systems you needed.



Thank you for choosing Hilti as your firestop experts!



 Best Regards,


Austin Griffith