Posted by Jose Munozabout 2 years ago
Fire penetration details for electrical conduits, ladder rack and cable tray for 4hr rated walls
I am looking for fire penetration details for electrical conduits, ladder rack and cable tray for 4hr rated walls. Can you provide a few options.
Thanks,
1 Reply
Posted by Nathaniel Crawfordabout 2 years ago
Hi Jose - You'll have a few options for 4-hr systems. CFS-COS is probably going to be your best bet for these conditions. I can only attach one system here, but I'll outline a couple systems for you to look up for these conditions. You can search for systems using the firestop selector on the Hilti Construction Platform at https://constructionplatform.hilti.com/
C-AJ-8250 - cable bundles and conduits
C-AJ-4107 - open ladder cable tray
Regards,
Nate Crawford - Lead FPE
