Posted by MARK PUCCIOalmost 3 years ago
Epoxy anchor pull out in wall modeling
Hello, I would like to use PROFIS to check epoxy tie anchors into a concrete wall. Anchors will be in tension. I see options for base plates and ledger angle but not this case given Hilti's less than user friendly platform I thought I would ask if an how to go about what should be a very simple model.
1 Reply
Posted by Danielle Fileralmost 3 years ago
Hi Mark,
There is the option to remove the base plate from the model in PROFIS Engineering. Additionally, the slab of concrete in PROFIS Engineering can represent a wall, floor, or ceiling. It is just dependent on how you input loads. If you have a unique situation, I recommend reaching out to Hilti's Engineering team to discuss your options. You can reach them at 877-749-6337 or hnatechnicalservices@hilti.com.
Regards,
Dani