Posted by Clare Chauabout 5 years ago
Embedment depth of HIT-V rods
Limit of 20d is set in Profis for design of post-fixed anchors, is there a minimum requirement for minimum embedment in-built in Profis? Which standards is this based on?
1 Reply
Posted by PARIS STANTONabout 5 years ago
Hi Clare,
Thank you for reaching out to us. The embedment depth limitations for adhesive anchors in PROFIS Engineering are from the code you are designing to, i.e. ACI or CSA. Please see snippet below from ACI 318-19 Chapter 17:
Regards,
Paris