Skip to main content

Embedment Depth Limits Cast-In-Place Anchor

Posted by MELISSA PEYTONabout 3 years ago
Embedment Depth Limits Cast-In-Place Anchor

I am getting an error that my, "embedment depth is outside approved values" for cast-in-place anchors. I'm using ACI 318-19. Can you please point me to the code section that has triggered this error? I'm trying to find an equivalent section in ACI 318-19 to D.4.2.2 from ACI 318-08.

ACI 318-19,cast-in-place embedment depth limits

2 Replies
Posted by Danielle Filerabout 3 years ago
Hilti Verified

Hi Melissa,

I'm not sure what error message you are receiving. I believe you are referring to the 25" embedment depth limitation, which comes from ACI 318-19 17.6.2.2.3. See the snip attached. If this is not the error message you were referring to, please email your .pe file to hnatechnicalservices@hilti.com for more assistance.

Regards,
Dani

cast-in-place embedment depth limits,ACI 318-19 17.6.2.2.3,25 embedment depth limitation,cast-in embedment depth

1 comment on this reply
Posted by MELISSA PEYTONabout 3 years ago
Thank you! Exactly what I was looking for.