During the process of drilling and grouting #5 rebar utilizing HIT-RE 500 V3, how deep should the embedment be?

Does this follow ACI development length? Dowels in a cast-in-place concrete foundation for CMU construction were missed, only solution is to drill and grout more dowels.

Post grouting,drilling through reinforcing

1 Reply
Posted by Ashley Couronabout 3 years ago
Hilti Verified

Hi Kordell,

The necessary embedment depth required will be based upon your specific application. Technical information for the HIT-RE 500 V3 with rebar can be found beginning on page 108 of Hilti's Anchor Fastening Product Technical Guide. If you are going to be designing using rebar development theory, information on this methodology can be found beginning on page 163 of the same guide.

Regards,
Ashley