Posted by Jenna Mecsejialmost 4 years ago
Critical Edge Distance

ESR 4868 (and others reports) give an equation to calculate Cac that states the equation comes from ACI 318, however these equations cannot be found. This comment refers to Eq. 17.6.5.5.1c for ACI 318-19, Eq 17.4.5.5c for ACI 318-14 and etc etc.

Is the equation for Cac something developed by Hilti? Where does it come from?

critical edge distance,Cac

1 Reply
Posted by Ashley Couronalmost 4 years ago
Hilti Verified

Hi Jenna,

Information regarding Cac can be found in a few sections within ACI 318-19. Critical edge distance can be found in Sections 17.9.5, 17.6.2.6, and 17.6.5.5. The commentary in Section 17.9.5 refers to product specific data for critical edge distance, which can be found the ESR documentation.

If you have further questions, please reach out to hnatechnicalservices@hilti.com.

Regards,
Ashley