Conduit sleeves for 3/4 Installed conduit

Posted by Dan Lindahlalmost 2 years ago
Conduit sleeves for 3/4 Installed conduit

There are 40 3/4" conduits already installed thru a firewall, they are tight to the concrete deck and they need to have a 1/2" barrier between the concrete and the top of the conduit. Is there a sleeve or assembly we can get that will give us this dimension and also achieve the 2 hr firestop rating required. Thanks.

conduit penetration,firestop material

1 Reply
Posted by Nathaniel Crawfordalmost 2 years ago
Hilti Verified

Hey Dan - We can address your application through an Engineering Judgment which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
 
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: hilti.com/ej (US) or hilti.ca/ej (Canada.) 

Regards,
Nate Crawford - Lead FPE