Skip to main content
Cart

Concrete is cracked with 0.3mm as per design with concrete strength is C40/50, is this suitable to use with Hilti HSA type?

Posted by sothea sorover 2 years ago
Concrete is cracked with 0.3mm as per design with concrete strength is C40/50, is this suitable to use with Hilti HSA type?

Concrete is cracked with 0.3mm as per design with concrete strength is C40/50, is this suitable to use with Hilti HSA type?

Cracked,with,0.3mm

1 Reply
Posted by Samantha Burtover 2 years ago
Hilti Verified

Hi Sothea,

The Hilti HSA anchor is not available in Hilti North America. Further support for this anchor should be sourced from the Hilti country that supplies the anchor and provides local technical data.

If you would like to consider the Hilti North America anchor portfolio, please reference the Anchor Fastening Technical Guide. Pages 10 and 11 provide a mechanical anchor selection guide.

Best,
Sam