Concrete edge failure calculation

Posted by Jamison Wilsonabout 2 years ago
Concrete edge failure calculation

Can you explain the calculations of Avc in the attached report (page5/8)? It looks like we should be able to use (4) Avc0 with the spacing and member depth. Please confirm.

concrete edge failure,projected area of anchor group

1 Reply
Posted by Matthew Fordabout 2 years ago
Hilti Verified

Hi Jamison,

For more information on how PROFIS Engineering calculates Avc when evaluating concrete edge failure, please reference page 191 of the PROFIS Engineering Design Guide.

For additional assistance, please reach out to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.

Regards,
Matthew

Profis engineering software