Posted by Mikeover 3 years ago
CMU size in PROFIS

Why is 8 inch CMU the only unit size available in PROFIS? I have anchors in a 12 inch wall I need to check

Hilit Profis,12 CMU

1 Reply
Posted by Ashley Couronover 3 years ago
Hilti Verified

Hi Mike,


Please see this answer from a previous question.


Regards,
Ashley



2 comments on this reply
Posted by Hilti Employeeabout 21 hours ago
Hi Liz, Thank you for reaching out. You can now change the CMU size (8-inch or 12-inch) for grout-filled CMU in the Anchoring to Masonry module in PROFIS Engineering. If you have any further questions, feel free to reach out to us at hnatechnicalservices@hilti.com or give us a call at 877-749-6337.  Regards, Kevin

Posted by Liz2 days ago
That link no longer works and I would also like to know the answer. Both 8 inch and 12 inch CMU are common sizes.