Skip to main content
Cart

Can mechanical anchors be installed in water saturated concrete?

Posted by Lee Sturdevantalmost 2 years ago
Can mechanical anchors be installed in water saturated concrete?

Can mechanical anchors (e.g., Kwik Bolts) be installed in water saturated concrete? I will be anchoring a plate in a concrete tank that has been just drained. I will not have much time before the tank will need to be refilled.

water-saturated concrete,mechanical anchoring system

1 Reply
Posted by Ashley Couronalmost 2 years ago
Hilti Verified

Hi Lee,

Hilti does not have any formal testing for mechanical anchors installed into water-saturated concrete. Hilti does have testing and approvals for adhesive anchors installed into water-saturated concrete which can be found beginning in Section 3.2.2 of Hilti's Anchor Fastening Product Technical Guide. Ultimately, all design decisions are up to the discretion of the Engineer of Record on the project.

If you would like to discuss the application further, please reach out via email to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.

Regards,
Ashley

water-saturated concrete,adhesive anchor system,mechanical anchor system