Can I select longer TZ2 anchor (and embedment)?

Posted by Kevin Dommeralmost 4 years ago
Can I select longer TZ2 anchor (and embedment)?

I'm trying to evaluate a long TZ anchor, but Profis limits the options for length. For example, I know I can order a TZ2 1/2"x10", but Profis options only go to maximum length of 4.5" (3.25 h_ef). Is there a way to increase the embedment used in Profis, or is there a reason we shouldn't be using long TZ2 with an increased embedment?

embedment length,KB TZ2

1 Reply
Posted by Emily almost 4 years ago
Hilti Verified

Hi Kevin,

Effective embedments are limited to those we have testing for; see Table 1 on page 6 of ESR-4266 for effective embedment options. Hilti offers longer anchors to account for variances in base plate thicknesses as well as nut and washers. Any embedment that is deeper than what is listed in its ESR is out of the scope of testing. Ultimately, all design decisions are up to the engineer of record.

Best Regards, 
Emily

effective embedment,KB-TZ2,anchor length

1 comment on this reply
Posted by Kevin Dommeralmost 4 years ago
Understood, thanks Emily!