Can CP 617 Firestop Putty Pad be used on elevator call buttons?

Posted by RAUDEL MARINalmost 2 years ago
Can CP 617 Firestop Putty Pad be used on elevator call buttons?

I'm installing an elevator call button in an existing 2-hour elevator shaft wall and want to maintain the 2-hour fire rating. Wondering if I can use the putty pad to maintain the fire rating. If so, is there an approved UL-listed system for the CP 617 Firestop Putty Pad ?

Call-button,putty-pad

1 Reply
Posted by Chase Hellanalmost 2 years ago

Hello, many times CP 617 Putty Pads can be used on elevator call boxes, however it will be determined by your onsite construction, and will require an Engineering Judgement (EJ). Please see below on how to submit an EJ request.
Thank you,
Chase Hellan
Sr. Fire Protection Engineer

Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: hilti.com/ej (US) or hilti.ca/ej (Canada.)