Calculating critical edge distance for Kwik Bolt TZ2's?

Posted by Tom Wallacealmost 2 years ago
Calculating critical edge distance for Kwik Bolt TZ2's?

Referring to ACI318-19, it appears critical edge distance is a function of effective embedment, but looking at the TZ2 ESR this does not appear to be the case. For example, two different diameter bolts with the same embedment (5/8 and 3/4" @3-1/4" embedment, for example) have significantly different critical edge distances. Additionally, Cac decreases as the embedment increases for multiple anchors. How are these calculated? I am asking because I am trying to calculate breakout strengths for embedment depths outside the PROFIS selected depths and need to be able to calculate this value.

critical edge distance,calculation,KB TZ2,Hilit Profis

1 Reply
Posted by Ashley Couronalmost 2 years ago
Hilti Verified

Hi Tom,

The critical edge distance for the KB-TZ2 for the various diameters and embedment depths found in ESR-4266 is determined through testing. If you decide to install the KB-TZ2 outside of the tested embedment depths for a specific diameter, that will be up to the engineering judgement of the Engineer of Record for the project.

If you have additional questions, please reach out to hnatechnicalservices@hilti.com.

Regards,
Ashley

KB-TZ2