Cac & Kc Values Inconsistent with A23.3 D6.2.2 for KH-EZ Anchors

Posted by Catlowover 3 years ago
Cac & Kc Values Inconsistent with A23.3 D6.2.2 for KH-EZ Anchors

The Critical Edge Distance and Concrete Breakout Coefficient are Calculated Incorrectly and Inconsistently Across Embedment Depths. Maximum k is 10 w/ Testing Typically 7 per D6.2.2. Listed in One or More Scenarios up to 17. Cac is Between 2.5 & 4*hef and is as low as 7.28". The Result is Some Embed Depths Show Adequate and Others Show Over Unity

Kcr Factor,Conccrete

1 Reply
Posted by Emily over 3 years ago
Hilti Verified

Hi,

For assistance please send your design reports as well as your .pe files to CA.EngineeringTechnicalServices@hilti.com so that we can further investigate.

Regards,
Emily