Why does Hilti Profis not use 1.0 for bond splitting factor for post-installed rebars (adhesive anchor) in tension when there is supplemental reinforcement in uncracked concrete ? The equations 17.6.5.5.1a & 17.6.5.5.1b in ACI 318-19 are only for uncracked concrete without supplementary reinforcement. This often causes the bond strength in cracked concrete to be higher than uncracked concrete.
Hi Sayantani,
Thank you for reaching out. Could you please send this question along with your PROFIS Engineering .pe file to hnatechnicalservices@hilti.com? They will be able to look into your file and provide input there.
Kind regards,
Sinan
Was there a resolution to this inquiry? The "supplementary reinforcement" section of user input does not appear to have an explicit "splitting supplementary reinforcement" check box (only shear and tension supplementary reinforcement). So when uncracked concrete is used, psi_cp,N can result in a value much lower than 1, even if the designer provides splitting reinforcement.