Posted by Owen Joyce over 4 years ago
Blazemaster tested to 50PA

Hi.
We are looking for a 1hr listing for Blazemaster piping (CPVC) 1 1/2" thick piping penetrating a one hour rated drywall wall.
With FS-One max and no wrap strip. System must be tested to 50Pa pressure differential

Similar to W-L-2678 but tested to 50

Thanks for the help

Blazemaster 50pa CPVC FS one,Blazemaster Firestop

1 Reply
Posted by Tyler Thomasover 4 years ago
Hilti Verified

Hello Owen,
Unfortunately, we don't have any listing for Blazemaster CPVC with FS-One max sealant only for 50pa pressure differential. It may be possible to issue an engineering judgment for 50pa with wrap strips. We will need to verify with the firestop testing department if that will work for you.
Best regards,
Tyler


1 comment on this reply
Posted by Owen Joyce over 4 years ago
Hi Tyler No thank you. Thanks for your work Owen