Posted by Arvin Manalaysayabout 3 years ago
Anchors for 6in CMU Wall

Does HILTI have any anchors that can be used satisfactory for a 6in CMU wall? HIT-HY 200-A and HIT-HY 270 both requires minimum nominal CMU thickness of 8in.

ANCHORS,Masony Adhesive Anchors

1 Reply
Posted by Danielle Filerabout 3 years ago
Hilti Verified

Hi Arvin,

All of Hilti's testing for CMU was performed in an 8 inch by 8 inch by 16 inch nominal CMU block. If you have a block that is less than that, it will be up to the Engineer of Record on the project and Hilti would recommend onsite testing.

Regards,
Dani

CMU nominal block size,8x8x16