Anchoring into the Face of Partially Grouted CMU Walls

Posted by Lewis Quigleyabout 4 years ago
Anchoring into the Face of Partially Grouted CMU Walls

I am testing out the new design for anchoring into masonry software and ran into a situation that I could not reconcile with the ESR report. For anchoring into a partially grouted wall (grouted at say 24" OC) I have conservatively idealized this as an 8" wide grouted masonry wall (see attached for reference). Loads perpendicular to the edge follow the ESR tables but when I try applying a load parallel to the edge there is a very small reduction factor (0.16) that causes the anchor to fail. Can you provide some insight into how the calculation is being performed in this case? Thanks.

masonry anchorage,anchoring in masonry

1 Reply
Posted by Ashley Couronabout 4 years ago
Hilti Verified

Hi Lewis,
 
For further assistance, please email your “.pe” file and PROFIS Engineering report to hnatechnicalservices@hilti.com.
 
Regards,
Ashley