Posted by Robert Chienabout 3 years ago
Anchorage to Concrete Edge Distance Requirement for Side Face Blowout Check
As shown in the file attached, the embed having an edge distance of 3" does not require a concrete side face blowout check. However, when the embed edge distance is reduced to 2.5" then suddenly the check is required. How come there is no required concrete side face blowout check for this case? I am asking because when the edge distance is reduced to 2.5 inches, the embed is failing in tension by 160% due to side face blowout where adding 0.5" calls for it to not be checked at all.
1 Reply
Posted by Danielle Filerabout 3 years ago
Hi Robert,
Can you please email me the .pe file at hnatechnicalservices@hilti.com so I can better assist?
Thanks,
Dani