anchor to 2000 psi concrete on DSA project

Posted by Jeff Haightover 3 years ago
anchor to 2000 psi concrete on DSA project

Do you have any anchors that have ESR reports suitable for anchoring 2x4 sill plates to a 2000 psi concrete slab on grade?

Anchoring,DSA

2 Replies
Posted by Samantha Burtover 3 years ago
Hilti Verified

Hi Jeff,

ICC ESR-2379 can be referenced for sill plate applications. Please note that the technical data is for a minimum 2,500 psi normal weight concrete. Hilti mechanical and adhesive anchor ESRs typically also have a lower limit of 2,500 psi, per ACI testing. 

Best,
Sam

Sill plate

1 comment on this reply
Posted by Jeff Haightover 3 years ago
Dear Samantha, Thank you for responding but the ESR notes 2500 psi minimum and as I mentioned I need an anchor that is approved for use in 2000 psi concrete. Does Hilti have a product that I can use in this application? Or do you have a recommendation on how I might justify the use of anchors that don't have ESR values in 2000 psi concrete? Jeff

Posted by Samantha Burtover 3 years ago

Hi Jeff,

Hilti does not have an approved product for 2,000 psi concrete. Hilti tested these fasteners per AC 70, Acceptance Criteria for Fasteners Power-Driven into Concrete, Steel, and Masonry Elements, where the 2,500 psi minimum is listed for sill plate applications. AC 70 is referenced in Section 6.0 of ESR-2379.

Onsite testing is recommended to justify if the fasteners are suitable for conditions outside of the ESR, such as lower strength concrete applications.

Best,
Sam


1 comment on this reply
Posted by Jeff Haightover 3 years ago
Thank you for the quick response.