Posted by Stanly Rosarioover 1 year ago
Anchor System Bridge Attachment

Good morning,

I hope this message finds you well. Currently we're preparing permit application to the installation of a 8" Fiberglass conduit attached under the bridge deck, and per FDOT we need to use an adhesive anchor system, so, I need to know the your helps with the following issue:

What type of anchors do you suggest for this type of job and what is the Minimum and maximun distance between anchors?

Thank you,

adhesive anchor,Minimum and maximun spacing

1 Reply
Posted by Matthew Fordover 1 year ago
Hilti Verified

Hi Stanly, 

HIT-RE 500 V3 and HIT-HY 200 V3 are frequently considered adhesive anchoring systems for applications into concrete base materials. Technical information is available in Hilti's Anchor Fastening Technical Guide, or in each anchor's respective Evaluation Service Report (ESR). These documents will contain the minimum anchor spacing requirements for each anchor, but please note that there is no maximum anchor spacing requirement. 

For additional assistance, please reach out to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.

Regards,
Matthew

Adhesive Anchoring Systems