Anchor Pryout in HILTI Profis

Posted by Zaqueo Salazarabout 2 years ago
Anchor Pryout in HILTI Profis

HILTI Profis uses the anchor breakout equations from section 17.6.2.1 to check the concrete strength for pryout forces on the anchors. This is allowed by ACI per section 17.7.3.1.1 or 17.7.3.1.2. However, since section 17.6.2.1 is checking the anchors in the breakout failure mode, why is there no increase in strength with the use of tension reinforcing? In fact with tension reinforcing present, the concrete should see minimal to no stress, correct? I would assume this would be the same as if the anchors were in tension and transferring the force to the tension bars in the pedestal. Please see attached calculation snapshot.

shear and tension pryout,anchor reinforcing

1 Reply
Posted by Ashley Couronabout 2 years ago
Hilti Verified

Hi Zaqueo,

For more information related to how PROFIS Engineering calculates concrete breakout, please refer to the PROFIS Engineering Design Guide beginning on page 48.

For additional assistance, please email your ".pe" file to hnatechnicalservices@hilti.com.

Regards,
Ashley

Profis engineering software