Anchor Plate Thickness for HIT-HY 200 V3 HIT-Z Application

Posted by Mustafa Numanogluabout 4 years ago
Anchor Plate Thickness for HIT-HY 200 V3 HIT-Z Application

Hi,

I'm trying to design a baseplate for a tube which will be connected to an existing foundation.
I'm using HIT-HY200 V3 HIT-Z but I'm getting the following warning "Acceptable fixture thickness with the given embedment depth is not covered by the standard product portfolio of the selected anchor (standard portfolio covers values between 0 in and 0.35 in). Please contact Hilti to discuss the feasibility of supply!"
I was wondering if I can use 1/2" or 3/4" thick plate, req'd embedment length is about 6".

Thank you.

baseplate thickness,HIT-HY 200 V3 HIT-Z Application,hit-z bolt

1 Reply
Posted by Ashley Couronabout 4 years ago
Hilti Verified

Hi Mustafa,
 
Are you using a grouted stand-off condition in PROFIS Engineering? This message sometimes appears if there is stand-off present. If so, this Ask Hilti discussion is an additional reference to describe the grouted stand-off calculations in PROFIS Engineering. If you are not using this condition, please reach out to hnatechnicalservices@hilti.com for further assistance.
 
Regards,
Ashley