Hi,

I’m looking at an anchor condition at the corner of a parapet which has Kwik bolts connected to a welded plate. I was wondering how I should be taking my edge distance when doing calculations. I'm looking at one side of the corner at a time. Attached are my two interpretations, are either of these correct? The wind load is perpendicular to the axis of the bolts towards the edge.

expansion Anchor,Edge distance,corner,parapet

1 Reply
Posted by Bryan Johnsonover 8 years ago
Hilti Verified

Christopher,

For the analysis of the edge distance considerations, a good reference would be the following similar question: https://ask.hilti.com/questions/edge-distance-for-adjacent-channel-anchors/arwsnk. Although the question is mainly focused on Anchor Channel, the methodology can still be considered for post-installed anchor systems.

If you have any additional questions, please feel free to contact us.