Anchor Hole Size on Base Plates

Posted by Uma Atlurialmost 5 years ago
Anchor Hole Size on Base Plates

The base plate holes for the anchors are too large(2" bolt needs 3.25" hole). AISC design guide-1 manual table 2.3 says these are minimum values. AISC manual table 14-2 says these are maximum. Can we reduce the hole size, if so what would be limit? what is ACI-318-14 recommended value on these anchor hole sizes? what is the typical hole sizes, the construction industry uses?

Anchor Hole Sizes on Base Plates with custom washers,what does Hiiti recommends on these anchor holes.,what is the recommended spacing of platesif we use special plates at bottom of the anchor bolts

1 Reply
Posted by PARIS STANTONalmost 5 years ago
Hilti Verified

Hello,

Please refer to this answer from a previous question. If you have further questions or concerns, please contact teamaskhilti.us@hilti.com.

Regards,
Paris